a possible solution is to define the mixing box as a thermal zone and connect this to your plant as desired.
Cheers
Achim
Von: esp-r-bounces at lists.strath.ac.uk [mailto:esp-r-bounces at lists.strath.ac.uk] Im Auftrag von Dimitrios Sfakianakis
Gesendet: Donnerstag, 23. Mai 2013 16:48
An: 'esp-r at lists.strath.ac.uk'
Betreff: [esp-r] Exhaust air converging from more than two zones.
Dear list,
I have a model with 10 zones and have set up a plant component network comprised by a mixing box, cooler, heater and a fan (much like the 'Component based HVAC' exemplar) . Air is supplied and exhausted from each zone and converges to a mixing box (converge) where a temperature sensor is located, according to which the operation of the heater and the cooler are controlled. Since the mixing box component only has two inlets I cannot use it to converge multiple exhaust ducts. Is there a way to converge all exhaust ducts to a single mixing box component in order to sense an 'average' temperature?
Kind regards,
-
Dimitrios Sfakianakis