[esp-r] 答复: Intergrated bld/mfs/plant simulation
Tang, David
David.Tang at owenscorning.com
Tue May 10 03:01:40 BST 2011
Try to run at sub second time step or the smallest you can.
发件人: esp-r-bounces at lists.strath.ac.uk [mailto:esp-r-bounces at lists.strath.ac.uk] 代表 Macdonald, Iain
发送时间: 2011年5月10日 4:29
收件人: 'esp-r at lists.strath.ac.uk'
主题: [esp-r] Intergrated bld/mfs/plant simulation
I have a ‘simple’ integrated problem with a single thermal zone, a plant description of an AHU and a flow network controlling the AHU fans and % of outdoor air. Strangely the thermal zone shows a ventilation loss of about 2 kW while the AHU fan is on and heating. Can anyone explain this?
Some details:
1) The heating coil does heat the supply air to its set point (checked in the plant results)
2) The zone air temperature (from building results) is less than the supply air temperature (from plant results)
3) The building results show both a sensible heating load and a ventilation loss
4) Flow results show the fans coming on and off at the correct time and balanced flow into/out of the thermal zone’s node
Any suggestions welcome…
Thanks,
Iain
The information contained in this communication and its attachment(s) is intended only for the use of the individual to whom it is addressed and may contain information that is privileged, confidential, or exempt from disclosure. If the reader of this message is not the intended recipient, you are hereby notified that any dissemination, distribution, or copying of this communication is strictly prohibited. If you have received this communication in error, please notify postmaster at owenscorning.com and delete the communication without retaining any copies. Thank you.
Translations available: http://www.owenscorning.com/emailfooter.html
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.strath.ac.uk/archives/esp-r/attachments/20110510/64b055c2/attachment.html
More information about the esp-r
mailing list