[esp-r] Re: Heating and Cooling Loads
Rodrigo Perez
rodrigo.jpg at gmail.com
Thu Sep 10 20:12:26 BST 2009
Felipe and David,
Simulating the same model proposed by David in DesingBuilder, I have the
following result:
Heating 8,99 Kw.
Cooling 2,44 Kw.
Kind Regards,
Rodrigo Perez.
_____
De: Felipe Durán [mailto:felipe at b-green.cl]
Enviado el: jueves, 10 de septiembre de 2009 14:39
Para: Felipe Durán
CC: Tang, David; esp-r at lists.strath.ac.uk; Tang, Kevin; leen peeters; Xing,
Nina; Rodrigo Perez
Asunto: Re: [esp-r] Re: Heating and Cooling Loads
David,
I made a mistake and I simulated with esp-r using London Climate.
The rectified cooling and heating loads using CHL_Santiago_IWEC.epw for the
1 zone 10x10x3 concrete box are:
IES_VE 14,66 kW (heating) 5.27 kW (cooling)
ESP-r 8,029 kW (heating) 2,24 kW (cooling)
Kind Regards,
Felipe Durán Palma
Arquitecto PUC, MPhil. U. Cambridge
Director de Proyectos y Asesorías
Obispo Donoso 5 oficina 62 - Providencia - Santiago
felipe at b-green.cl - www.b-green.cl - 56 (2) 3431868
El 10 Sep 2009, a las 13:31, Felipe Durán escribió:
David,
Thank you for your help.
The results of the 1 zone 10x10x3 concrete box are:
IES_VE 14,66 kW (heating) 5,27 kW (cooling)
ESP-r 11,90 kW (heating) 1,86 kW (cooling)
1. Geometry: 1 zones of 10 m x 10 m x 3 m high.
2. Materials (outside to inside)
2.1 External Wall: Cast Concrete 0,2m, U-value = 3,1963 (W/m2K)
2.2 Roof: Cast Concrete 0,2 U-value = 3,5354 (W/m2K)
2.3 Ground Floor: Cast Concrete 0.2 m, U-value = 2.8340 (W/m2K)
3. Boundary Conditions: All the walls and the roof faces the outside. The
ground floor faces the ground.
4. Run Period: 1/1 31/12 (whole year)
5.No Internal gains
6. Climate file CHL_Santiago_IWEC.epw (from the energyplus database)
7. Comfort band 20 Cº-24Cº, on Heating and Cooling Profile: continiously
8. No Ventilation
Thank you again
Felipe Durán Palma
Arquitecto PUC, MPhil. U. Cambridge
Director de Proyectos y Asesorías
<pastedGraphic.tiff>
Obispo Donoso 5 oficina 62 - Providencia - Santiago
felipe at b-green.cl - www.b-green.cl - 56 (2) 3431868
El 9 Sep 2009, a las 22:56, Tang, David escribió:
Felipe,
I'd like to start with your 'a zone of 10 x 10 x 3 mt. high with no
ventilation and no internal gains' model which is an excellent case to
evaluate the fundamental algorithms.
Please provide info of that model likewise.
Having worked at IES-VE for 8+ years and coded part of Apache-sim and the
whole of macroflo, it is interesting to see how it works from user's point
of view.
Regards,
David Tang
Chief Engineer, Energy Solutions
Owens Corning
T: +86 21 6101 9587; F: +86 21 6101 9588; m: +86 13817249419
From: Felipe Durán [mailto:felipe at b-green.cl]
Sent: Thursday, September 10, 2009 1:01 AM
To: Tang, David
Cc: leen peeters; Tang, Kevin; Xing, Nina; esp-r at lists.strath.ac.uk; Rodrigo
Perez
Subject: Re: [esp-r] Re: Heating and Cooling Loads
David and Rodrigo,
Thank you for your help.
I`ve simplify the model and the results of the 3-floor office building are:
IES_VE 390 kW (heating) 123 kW (cooling)
ESP-r 246 kW (heating) 205 kW (cooling)
The model conditions of the 3-floor office building are:
IES_VE 390 kW (heating) 123 kW (cooling)
1. Geometry: 3 zones of 25 m x 60 m x 2.5 m high. 40% of glazing ratio for
all the orientations
2. Orientation: North towards the long side (25 meters)
3. Materials (outside to inside)
3.1 External Wall: cast concrete 0,2m, Polystyrene 0.02m, Gypsum
Plasterboard 0,01m. U-value = 0.9597 (W/m2K)
3.2 Window: Double glazing, clear float 6mm + 12mm cavity. U-Value=2.82
(W/m2K)
3.3 Roof: Cast concrete (lightweight) 0.05m, Polystyrene 0.15m, cast
concrete 0,15m. U-value = 0.1859 (W/m2K)
3.4 Ground Floor: Cast Concrete 0.15 m, polystyrene 0.05 m, U-value = 0.5041
(W/m2K)
3.5 Slabs: cast Concrete 0.15, U-value = 3,2558 (W/m2K)
4. Boundary Conditions: All the walls and the roof faces the outside. The
slabs are interiors and only the ground floor faces the grund.
5. Run Period: 1/1 31/12 (whole year)
6. Internal gains: Occupancy 6 m2/person (70 W Sensible, 35 W latent),
Lighting 8 W/m2, Equipment 5 W7m2. All the time for the whole year,
including nights, weekends, etc.
7. Climate file CHL_Santiago_IWEC.epw (from the energyplus database)
8. Comfort band 20 Cº-24Cº
9. Ventilation: infiltration 0.25 (ach/h), auxiliari ventilatios 3.25
(ach/h) on ESP-r infiltration of 3.25 (ach/h)
Thank you again
Felipe Durán Palma
Arquitecto PUC, MPhil. U. Cambridge
Director de Proyectos y Asesorías
Obispo Donoso 5 oficina 62 - Providencia - Santiago
felipe at b-green.cl - www.b-green.cl - 56 (2) 3431868
El 9 Sep 2009, a las 00:22, Tang, David escribió:
Describe your model we'll run DOE2 and EnergyPlus to see who's right.
geometry,
orientation
wall, window, roof materials,
boundary conditions (is the wall contact outside, ground, other indoor
space?)
run period (from mm/dd to mm/dd),
etc.
as detail as possible.
Regards,
David Tang
Chief Engineer, Energy Solutions
Owens Corning
T: +86 21 6101 9587; F: +86 21 6101 9588; m: +86 13817249419
From: esp-r-bounces at lists.strath.ac.uk
[mailto:esp-r-bounces at lists.strath.ac.uk] On Behalf Of Felipe Durán
Sent: Wednesday, September 09, 2009 5:10 AM
To: leen peeters
Cc: esp-r at lists.strath.ac.uk
Subject: [esp-r] Re: Heating and Cooling Loads
Leen,
I am working with the EPW climate file of Santiago de Chile in both soft
wares. I ve modelled a zone of 10 x 10 x 3 mt. high with no ventilation and
no internal gains. The results are:
ESP-r = 11.9 (heating), 1.86 (cooling)
IES = 14.6 (heating), 5.2 (cooling)
Now we got great differences in the cooling load. IES gave me 3 times more
cooling loads than ESP-r
Any ideas how to go proceed?
Felipe Durán Palma
Arquitecto PUC, MPhil. U. Cambridge
Director de Proyectos y Asesorías
Obispo Donoso 5 oficina 62 - Providencia - Santiago
felipe at b-green.cl - www.b-green.cl - 56 (2) 3431868
El 8 Sep 2009, a las 16:49, leen peeters escribió:
Felipe,
set you climate to some artifical constant climqte with constant
temperature, constant solar radiation,... That is one more set of variables
excluded
Leen
2009/9/8 Felipe Durán <felipe at b-green.cl>
Dear Samuel and Leen,
Actually, when I found out such big differences I ve modelled a very simple
3-zone model and the differences persist.
I will try out with a simple box without ventilation and internal gains and
I will let you know the results.
Thank you all for your help.
Felipe Durán Palma
Arquitecto PUC, MPhil. U. Cambridge
Director de Proyectos y Asesorías
<pastedGraphic.tiff>
Obispo Donoso 5 oficina 62 - Providencia - Santiago
felipe at b-green.cl - www.b-green.cl <http://www.b-green.cl/> - 56 (2)
3431868
El 8 Sep 2009, a las 13:19, Aizaz Samuel escribió:
Try reducing your model complexity by modelling just one zone with minimal
information possible. Simulate for just one day. If the two softwares
compare
well keep building up the model in complexity.
-Aizaz
On Tuesday 08 September 2009 17:41, Felipe Durán wrote:
Dear All,
I am modeling in both ESP-r and IES-VE and office building and the results
for heating and cooling loads are very different.
ESP-r = 269 kW (heating); 237 kW (cooling)
IES-VE = 835 kW (Heating); 360 kW (cooling)
Does anyone had a similar experience with such differences?
Kind Regards,
Felipe Durán Palma
Arquitecto PUC, MPhil. U. Cambridge
Director de Proyectos y Asesorías
[cid:B9AD3F91-76F4-4F37-8A2C-7A559281C059
<http://mail.google.com/mail/?ui=2&ik=8c428781db&view=att&th=1239aec006a1c65
8&attid=0.0.1.1&disp=emb&zw> ]
Obispo Donoso 5 oficina 62 - Providencia - Santiago
felipe at b-green.cl<mailto:felipe at b-green.cl> -
www.b-green.cl<http://www.b-green.cl <http://www.b-green.cl/> > - 56 (2)
3431868
The information contained in this communication and its attachment(s) is
intended only for the use of the individual to whom it is addressed and
may contain information that is privileged, confidential, or exempt from
disclosure. If the reader of this message is not the intended recipient,
you are hereby notified that any dissemination, distribution, or copying of
this communication is strictly prohibited. If you have received this
communication in error, please notify postmaster at owenscorning.com and delete
the communication without retaining any copies. Thank you.
Translations available: http://www.owenscorning.com/emailfooter.html
_______________________________________________
esp-r mailing list
esp-r at lists.strath.ac.uk
http://lists.strath.ac.uk/mailman/listinfo/esp-r
_______________________________________________
esp-r mailing list
esp-r at lists.strath.ac.uk
http://lists.strath.ac.uk/mailman/listinfo/esp-r
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.strath.ac.uk/archives/esp-r/attachments/20090910/3a4246cf/attachment-0001.html
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 61580 bytes
Desc: not available
Url : http://lists.strath.ac.uk/archives/esp-r/attachments/20090910/3a4246cf/attachment-0002.jpe
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1757 bytes
Desc: not available
Url : http://lists.strath.ac.uk/archives/esp-r/attachments/20090910/3a4246cf/attachment-0003.jpe
More information about the esp-r
mailing list