Dear Francesco,<br>
<br>
As far as I can ascertain from the ESP-r code, the MRT calculation does
not take account of emissivity. The default MRT is simply the area
weighted surface temperatures (subroutine MOMNRD in temps.F in
esrures). <br>
<br>
It is possible to specify MRT calculations at specific points in the
zone (using sensor "cubes"), in which case the calculation includes
viewfactors and 4th power radiant exchange (subroutine SENMRT in
temps.F in esrures) - but again emissivity is not included. Although
rather out-of-date in terms of the user interface, the following
publication on the ESRU website gives the basis of the method for
user-defined positions for MRT sensors:
<a class="moz-txt-link-freetext" href="http://www.esru.strath.ac.uk/Documents/ESPmrt.pdf">http://www.esru.strath.ac.uk/Documents/ESPmrt.pdf</a><br>
<br>
Regards<br>
Paul<br>
<br>
Francesco Frontini wrote:
<blockquote
 cite="mid:!~!UENERkVCMDkAAQACAAAAAAAAAAAAAAAAABgAAAAAAAAAru7KqoPmvUiwJBhxMD9pLMKAAAAQAAAAUa6zXH6QPEm9TJ19xKXRDgEAAAAA@polimi.it"
 type="cite">
  <pre wrap="">Dear Jon,
Ok, 
but where I can found the fomula used by ESP-r for the MRT calculation?
Best regards
Francesco

-----Messaggio originale-----
Da: <a class="moz-txt-link-abbreviated" href="mailto:esp-r-bounces@lists.strath.ac.uk">esp-r-bounces@lists.strath.ac.uk</a>
[<a class="moz-txt-link-freetext" href="mailto:esp-r-bounces@lists.strath.ac.uk">mailto:esp-r-bounces@lists.strath.ac.uk</a>] Per conto di
<a class="moz-txt-link-abbreviated" href="mailto:esp-r-request@lists.strath.ac.uk">esp-r-request@lists.strath.ac.uk</a>
Inviato: marted&igrave; 20 maggio 2008 13.00
A: <a class="moz-txt-link-abbreviated" href="mailto:esp-r@lists.strath.ac.uk">esp-r@lists.strath.ac.uk</a>
Oggetto: esp-r Digest, Vol 22, Issue 15

Send esp-r mailing list submissions to
        <a class="moz-txt-link-abbreviated" href="mailto:esp-r@lists.strath.ac.uk">esp-r@lists.strath.ac.uk</a>

To subscribe or unsubscribe via the World Wide Web, visit
        <a class="moz-txt-link-freetext" href="http://lists.strath.ac.uk/mailman/listinfo/esp-r">http://lists.strath.ac.uk/mailman/listinfo/esp-r</a>
or, via email, send a message with subject or body 'help' to
        <a class="moz-txt-link-abbreviated" href="mailto:esp-r-request@lists.strath.ac.uk">esp-r-request@lists.strath.ac.uk</a>

You can reach the person managing the list at
        <a class="moz-txt-link-abbreviated" href="mailto:esp-r-owner@lists.strath.ac.uk">esp-r-owner@lists.strath.ac.uk</a>

When replying, please edit your Subject line so it is more specific than
"Re: Contents of esp-r digest..."


Today's Topics:

   1.  Mean Radiant Temperature (<a class="moz-txt-link-abbreviated" href="mailto:francesco.frontini@polimi.it">francesco.frontini@polimi.it</a>)
   2. Re: Mean Radiant Temperature (Geissler Achim)
   3.  R:   Mean Radiant Temperature (Francesco Frontini)
   4. Re: R:   Mean Radiant Temperature (Geissler Achim)
   5. Re: R:   Mean Radiant Temperature (Jon Hand)


----------------------------------------------------------------------

Message: 1
Date: Tue, 20 May 2008 08:45:52 +0200
From: <a class="moz-txt-link-abbreviated" href="mailto:francesco.frontini@polimi.it">francesco.frontini@polimi.it</a>
Subject: [esp-r]  Mean Radiant Temperature
To: <a class="moz-txt-link-abbreviated" href="mailto:esp-r@lists.strath.ac.uk">esp-r@lists.strath.ac.uk</a>
Message-ID: <a class="moz-txt-link-rfc2396E" href="mailto:20080520084552.y2yaryo9kcs880ks@webmail.polimi.it">&lt;20080520084552.y2yaryo9kcs880ks@webmail.polimi.it&gt;</a>
Content-Type: text/plain;        charset=ISO-8859-1;        DelSp="Yes";
        format="flowed"

Dear All,
I have a question about MRT.

We want to assess the impact on the operative temperature in an office if we
use an internal blind with a low-emissivity coating (0,5 emissivity for
indoor-facing surface) instead of 0.9 emissivity.
We made two different simulation: static (with WIS program) and Dynamic
(ESP-r).

The results from WIS and from ESP-R for the blind surface temperature are
consistent (blind temperature about 5K higher for the low-emissivity blind).
However, the mean radiant temperature at a position close to the blind (0.5
m in ESP-R) is lower for the high-emissivity blind than the low-emissivity
blind with the ESP-R calculation.
Could you please send me the formula that ESP-r uses for the MRT
calculation? Is there any approximation that would not be appropriate for
low-emissivity surfaces?

I model the double glazing fa?ade with the internal blind like a single
construction (no air-ventilation between the glass and the blind). I set the
U-value for each fa?ade construction (it is similar but not identical for
the two different solutions, U=0,985+-0,005, obtained from the WIS
calculation), and the g-value. What changes in the model is the emissivity
of the indoor-facing surface of the blind
(e=0,9 for the first case and e=0,5 for the second one!), whereas the
solar-optical properties remain the same for the two blinds. In the WIS
model, the emissivity of the two blind surfaces is specified separately.
For both blinds, the emissivity of the outdoor-facing surface in the WIS
model is 0.9.


Looking forward to your answer and thanking you for your help.
Any advice and help on this will be much appreciated.

Francesco Frontini






------------------------------

Message: 2
Date: Tue, 20 May 2008 09:22:39 +0200
From: "Geissler Achim" <a class="moz-txt-link-rfc2396E" href="mailto:Achim.Geissler@josef-gartner.ch">&lt;Achim.Geissler@josef-gartner.ch&gt;</a>
Subject: [esp-r] Re: Mean Radiant Temperature
To: <a class="moz-txt-link-rfc2396E" href="mailto:francesco.frontini@polimi.it">&lt;francesco.frontini@polimi.it&gt;</a>,        <a class="moz-txt-link-rfc2396E" href="mailto:esp-r@lists.strath.ac.uk">&lt;esp-r@lists.strath.ac.uk&gt;</a>
Message-ID:
        <a class="moz-txt-link-rfc2396E" href="mailto:5410907208A9F149ADB6E44744892B3C45EBE8@sgartgum1.gart.intra">&lt;5410907208A9F149ADB6E44744892B3C45EBE8@sgartgum1.gart.intra&gt;</a>
Content-Type: text/plain;        charset="iso-8859-1"

Dear Francesco,

  </pre>
  <blockquote type="cite">
    <pre wrap="">We want to assess the impact on the operative temperature in an office 
if we use an internal blind with a low-emissivity coating (0,5 
emissivity for indoor-facing surface) instead of 0.9 emissivity.
We made two different simulation: static (with WIS program) and 
Dynamic (ESP-r).
    </pre>
  </blockquote>
  <pre wrap=""><!---->
  </pre>
  <blockquote type="cite">
    <pre wrap="">The results from WIS and from ESP-R for the blind surface temperature 
are consistent (blind temperature about 5K higher for the 
low-emissivity blind).
    </pre>
  </blockquote>
  <pre wrap=""><!---->That is good news.

  </pre>
  <blockquote type="cite">
    <pre wrap="">However, the mean radiant temperature at a position close to the blind 
(0.5 m in ESP-R) is lower for the high-emissivity blind than the 
low-emissivity blind with the ESP-R calculation.
    </pre>
  </blockquote>
  <pre wrap=""><!---->
As the mean radiant temperature is defined by view factors and surface
temperature, only, all is well, no? The low-e blind has a higher
temperature, thus I would expect the mean radiant temperature close to the
blind to be higher. That is what you seem to have obtained as result?

Best regards,
Achim





------------------------------

Message: 3
Date: Tue, 20 May 2008 10:35:15 +0200
From: "Francesco Frontini" <a class="moz-txt-link-rfc2396E" href="mailto:francesco.frontini@polimi.it">&lt;francesco.frontini@polimi.it&gt;</a>
Subject: [esp-r]  R:   Mean Radiant Temperature
To: "'Geissler Achim'" <a class="moz-txt-link-rfc2396E" href="mailto:Achim.Geissler@josef-gartner.ch">&lt;Achim.Geissler@josef-gartner.ch&gt;</a>,
        <a class="moz-txt-link-rfc2396E" href="mailto:esp-r@lists.strath.ac.uk">&lt;esp-r@lists.strath.ac.uk&gt;</a>
Message-ID:
        
&lt;!~!UENERkVCMDkAAQACAAAAAAAAAAAAAAAAABgAAAAAAAAAru7KqoPmvUiwJBhxMD9pLMKAAAAQ
<a class="moz-txt-link-abbreviated" href="mailto:AAAAq+fYsqTr4E+5QjbiDeTAbQEAAAAA@polimi.it">AAAAq+fYsqTr4E+5QjbiDeTAbQEAAAAA@polimi.it</a>&gt;
        
Content-Type: text/plain;        charset="iso-8859-1"

Dear Achim
Yes I have obtained a MRT, close to the blind, higher for the solution with
low-e blind (that has a higer surface temperature). But for my opinion the
MRT has to take into account not only the view factor and the temperature of
the surface but also the emissivity. For that reason I'm also supposing that
with a low emmissivity also the MRT should be low (for exemple if the view
factor is the same: 43,88?x0,9&gt;48.21?x0,5! Where the formula is
(T1(?C)blind)*(emissivity(1))&gt;(T2(?C)blind)*(emissivity(2))!!!). It's not
correct?

Best regards,
Francesco

-----Messaggio originale-----
Da: Geissler Achim [<a class="moz-txt-link-freetext" href="mailto:Achim.Geissler@josef-gartner.ch">mailto:Achim.Geissler@josef-gartner.ch</a>]
Inviato: marted? 20 maggio 2008 9.23
A: <a class="moz-txt-link-abbreviated" href="mailto:francesco.frontini@polimi.it">francesco.frontini@polimi.it</a>; <a class="moz-txt-link-abbreviated" href="mailto:esp-r@lists.strath.ac.uk">esp-r@lists.strath.ac.uk</a>
Oggetto: RE: [esp-r] Mean Radiant Temperature

Dear Francesco,

  </pre>
  <blockquote type="cite">
    <pre wrap="">We want to assess the impact on the operative temperature in an office 
if we use an internal blind with a low-emissivity coating (0,5 
emissivity for indoor-facing surface) instead of 0.9 emissivity.
We made two different simulation: static (with WIS program) and 
Dynamic (ESP-r).
    </pre>
  </blockquote>
  <pre wrap=""><!---->
  </pre>
  <blockquote type="cite">
    <pre wrap="">The results from WIS and from ESP-R for the blind surface temperature 
are consistent (blind temperature about 5K higher for the 
low-emissivity blind).
    </pre>
  </blockquote>
  <pre wrap=""><!---->That is good news.

  </pre>
  <blockquote type="cite">
    <pre wrap="">However, the mean radiant temperature at a position close to the blind
(0.5 m in ESP-R) is lower for the high-emissivity blind than the 
low-emissivity blind with the ESP-R calculation.
    </pre>
  </blockquote>
  <pre wrap=""><!---->
As the mean radiant temperature is defined by view factors and surface
temperature, only, all is well, no? The low-e blind has a higher
temperature, thus I would expect the mean radiant temperature close to the
blind to be higher. That is what you seem to have obtained as result?

Best regards,
Achim





------------------------------

Message: 4
Date: Tue, 20 May 2008 11:33:33 +0200
From: "Geissler Achim" <a class="moz-txt-link-rfc2396E" href="mailto:Achim.Geissler@josef-gartner.ch">&lt;Achim.Geissler@josef-gartner.ch&gt;</a>
Subject: [esp-r] Re: R:   Mean Radiant Temperature
To: "Francesco Frontini" <a class="moz-txt-link-rfc2396E" href="mailto:francesco.frontini@polimi.it">&lt;francesco.frontini@polimi.it&gt;</a>,
        <a class="moz-txt-link-rfc2396E" href="mailto:esp-r@lists.strath.ac.uk">&lt;esp-r@lists.strath.ac.uk&gt;</a>
Message-ID:
        <a class="moz-txt-link-rfc2396E" href="mailto:5410907208A9F149ADB6E44744892B3C45EC09@sgartgum1.gart.intra">&lt;5410907208A9F149ADB6E44744892B3C45EC09@sgartgum1.gart.intra&gt;</a>
Content-Type: text/plain;        charset="iso-8859-1"

Dear Francesco,
the definitions I know of for mean radiant temperature do not take
emissivity into account. The interesting question probably is, is the
measure "MRT" useful for environments with large differences in emissivity?
Of course, for radiation heat transfer, the emissivity is important (that is
what I think you want to describe?).
I would assume that the definition of MRT is based on the "normal" case,
that all surfaces of an indoor space have an emissivity of approx. 0.9.
Thus, the description of the radiative surroundings by temperature alone is
sufficient.
For your case, you may need to define a "new" MRT - maybe more a "mean
radiant heat exchange" type of coefficient (or try PPD / PMV calculations,
however, these also use standard mean radiant temperature for their
calculation).
Regards,
Achim


  </pre>
  <blockquote type="cite">
    <pre wrap="">-----Original Message-----
From: <a class="moz-txt-link-abbreviated" href="mailto:esp-r-bounces@lists.strath.ac.uk">esp-r-bounces@lists.strath.ac.uk</a> [<a class="moz-txt-link-freetext" href="mailto:esp-r">mailto:esp-r</a>- 
<a class="moz-txt-link-abbreviated" href="mailto:bounces@lists.strath.ac.uk">bounces@lists.strath.ac.uk</a>] On Behalf Of Francesco Frontini
Sent: Tuesday, May 20, 2008 10:35 AM
To: Geissler Achim; <a class="moz-txt-link-abbreviated" href="mailto:esp-r@lists.strath.ac.uk">esp-r@lists.strath.ac.uk</a>
Subject: [esp-r] R: Mean Radiant Temperature

Dear Achim
Yes I have obtained a MRT, close to the blind, higher for the solution 
with low-e blind (that has a higer surface temperature). But for my 
opinion the MRT has to take into account not only the view factor and 
the temperature of the surface but also the emissivity. For that 
reason I'm also supposing that with a low emmissivity also the MRT 
should be low (for exemple if the view factor is the same: 
43,88?x0,9&gt;48.21?x0,5! Where the formula is 
(T1(?C)blind)*(emissivity(1))&gt;(T2(?C)blind)*(emissivity(2))!!!). It's 
not correct?

Best regards,
Francesco

-----Messaggio originale-----
Da: Geissler Achim [<a class="moz-txt-link-freetext" href="mailto:Achim.Geissler@josef-gartner.ch">mailto:Achim.Geissler@josef-gartner.ch</a>]
Inviato: marted? 20 maggio 2008 9.23
A: <a class="moz-txt-link-abbreviated" href="mailto:francesco.frontini@polimi.it">francesco.frontini@polimi.it</a>; <a class="moz-txt-link-abbreviated" href="mailto:esp-r@lists.strath.ac.uk">esp-r@lists.strath.ac.uk</a>
Oggetto: RE: [esp-r] Mean Radiant Temperature

Dear Francesco,

    </pre>
    <blockquote type="cite">
      <pre wrap="">We want to assess the impact on the operative temperature in an 
office if we use an internal blind with a low-emissivity coating 
(0,5 emissivity for indoor-facing surface) instead of 0.9 emissivity.
We made two different simulation: static (with WIS program) and 
Dynamic (ESP-r).
      </pre>
    </blockquote>
    <blockquote type="cite">
      <pre wrap="">The results from WIS and from ESP-R for the blind surface 
temperature are consistent (blind temperature about 5K higher for 
the low-emissivity blind).
      </pre>
    </blockquote>
    <pre wrap="">That is good news.

    </pre>
    <blockquote type="cite">
      <pre wrap="">However, the mean radiant temperature at a position close to the 
blind
(0.5 m in ESP-R) is lower for the high-emissivity blind than the 
low-emissivity blind with the ESP-R calculation.
      </pre>
    </blockquote>
    <pre wrap="">As the mean radiant temperature is defined by view factors and surface 
temperature, only, all is well, no? The low-e blind has a higher 
temperature, thus I would expect the mean radiant temperature close to 
the blind to be higher. That is what you seem to have obtained as result?

Best regards,
Achim



_______________________________________________
esp-r mailing list
<a class="moz-txt-link-abbreviated" href="mailto:esp-r@lists.strath.ac.uk">esp-r@lists.strath.ac.uk</a>
<a class="moz-txt-link-freetext" href="http://lists.strath.ac.uk/mailman/listinfo/esp-r">http://lists.strath.ac.uk/mailman/listinfo/esp-r</a>
    </pre>
  </blockquote>
  <pre wrap=""><!---->


------------------------------

Message: 5
Date: Tue, 20 May 2008 11:36:21 +0100
From: Jon Hand <a class="moz-txt-link-rfc2396E" href="mailto:jon@esru.strath.ac.uk">&lt;jon@esru.strath.ac.uk&gt;</a>
Subject: [esp-r] Re: R:   Mean Radiant Temperature
To: "Geissler Achim" <a class="moz-txt-link-rfc2396E" href="mailto:Achim.Geissler@josef-gartner.ch">&lt;Achim.Geissler@josef-gartner.ch&gt;</a>,        "Francesco
        Frontini" <a class="moz-txt-link-rfc2396E" href="mailto:francesco.frontini@polimi.it">&lt;francesco.frontini@polimi.it&gt;</a>,
<a class="moz-txt-link-rfc2396E" href="mailto:esp-r@lists.strath.ac.uk">&lt;esp-r@lists.strath.ac.uk&gt;</a>
Message-ID:
        <a class="moz-txt-link-rfc2396E" href="mailto:B94620A0857DFE4DB194C4A2DBDC088F8B5FD6@BE-SCAM2.ds.strath.ac.uk">&lt;B94620A0857DFE4DB194C4A2DBDC088F8B5FD6@BE-SCAM2.ds.strath.ac.uk&gt;</a>
Content-Type: text/plain; charset="iso-8859-1"


There is a radiant asymmetry report as part of the comfort report and I
think that will be taking account of the emissivity.

There is an esp-r model which deals with a heated ceiling panel and location
specific comfort for a patient in a bed which needs to be added as an
exemplar model. 

-Jon Hand


-----Original Message-----
From: <a class="moz-txt-link-abbreviated" href="mailto:esp-r-bounces@lists.strath.ac.uk">esp-r-bounces@lists.strath.ac.uk</a> on behalf of Geissler Achim
Sent: Tue 5/20/2008 10:33 AM
To: Francesco Frontini; <a class="moz-txt-link-abbreviated" href="mailto:esp-r@lists.strath.ac.uk">esp-r@lists.strath.ac.uk</a>
Subject: [esp-r] Re: R:   Mean Radiant Temperature
 
Dear Francesco,
the definitions I know of for mean radiant temperature do not take
emissivity into account. The interesting question probably is, is the
measure "MRT" useful for environments with large differences in emissivity?
Of course, for radiation heat transfer, the emissivity is important (that is
what I think you want to describe?).
I would assume that the definition of MRT is based on the "normal" case,
that all surfaces of an indoor space have an emissivity of approx. 0.9.
Thus, the description of the radiative surroundings by temperature alone is
sufficient.
For your case, you may need to define a "new" MRT - maybe more a "mean
radiant heat exchange" type of coefficient (or try PPD / PMV calculations,
however, these also use standard mean radiant temperature for their
calculation).
Regards,
Achim


  </pre>
  <blockquote type="cite">
    <pre wrap="">-----Original Message-----
From: <a class="moz-txt-link-abbreviated" href="mailto:esp-r-bounces@lists.strath.ac.uk">esp-r-bounces@lists.strath.ac.uk</a> [<a class="moz-txt-link-freetext" href="mailto:esp-r">mailto:esp-r</a>- 
<a class="moz-txt-link-abbreviated" href="mailto:bounces@lists.strath.ac.uk">bounces@lists.strath.ac.uk</a>] On Behalf Of Francesco Frontini
Sent: Tuesday, May 20, 2008 10:35 AM
To: Geissler Achim; <a class="moz-txt-link-abbreviated" href="mailto:esp-r@lists.strath.ac.uk">esp-r@lists.strath.ac.uk</a>
Subject: [esp-r] R: Mean Radiant Temperature

Dear Achim
Yes I have obtained a MRT, close to the blind, higher for the solution 
with low-e blind (that has a higer surface temperature). But for my 
opinion the MRT has to take into account not only the view factor and 
the temperature of the surface but also the emissivity. For that 
reason I'm also supposing that with a low emmissivity also the MRT 
should be low (for exemple if the view factor is the same: 
43,88?x0,9&gt;48.21?x0,5! Where the formula is 
(T1(?C)blind)*(emissivity(1))&gt;(T2(?C)blind)*(emissivity(2))!!!). It's 
not correct?

Best regards,
Francesco

-----Messaggio originale-----
Da: Geissler Achim [<a class="moz-txt-link-freetext" href="mailto:Achim.Geissler@josef-gartner.ch">mailto:Achim.Geissler@josef-gartner.ch</a>]
Inviato: marted? 20 maggio 2008 9.23
A: <a class="moz-txt-link-abbreviated" href="mailto:francesco.frontini@polimi.it">francesco.frontini@polimi.it</a>; <a class="moz-txt-link-abbreviated" href="mailto:esp-r@lists.strath.ac.uk">esp-r@lists.strath.ac.uk</a>
Oggetto: RE: [esp-r] Mean Radiant Temperature

Dear Francesco,

    </pre>
    <blockquote type="cite">
      <pre wrap="">We want to assess the impact on the operative temperature in an 
office if we use an internal blind with a low-emissivity coating 
(0,5 emissivity for indoor-facing surface) instead of 0.9 emissivity.
We made two different simulation: static (with WIS program) and 
Dynamic (ESP-r).
      </pre>
    </blockquote>
    <blockquote type="cite">
      <pre wrap="">The results from WIS and from ESP-R for the blind surface 
temperature are consistent (blind temperature about 5K higher for 
the low-emissivity blind).
      </pre>
    </blockquote>
    <pre wrap="">That is good news.

    </pre>
    <blockquote type="cite">
      <pre wrap="">However, the mean radiant temperature at a position close to the 
blind
(0.5 m in ESP-R) is lower for the high-emissivity blind than the 
low-emissivity blind with the ESP-R calculation.
      </pre>
    </blockquote>
    <pre wrap="">As the mean radiant temperature is defined by view factors and surface 
temperature, only, all is well, no? The low-e blind has a higher 
temperature, thus I would expect the mean radiant temperature close to 
the blind to be higher. That is what you seem to have obtained as result?

Best regards,
Achim



_______________________________________________
esp-r mailing list
<a class="moz-txt-link-abbreviated" href="mailto:esp-r@lists.strath.ac.uk">esp-r@lists.strath.ac.uk</a>
<a class="moz-txt-link-freetext" href="http://lists.strath.ac.uk/mailman/listinfo/esp-r">http://lists.strath.ac.uk/mailman/listinfo/esp-r</a>
    </pre>
  </blockquote>
  <pre wrap=""><!----></pre>
</blockquote>
<br>
</body>
</html>