Dear Dimitrios,
what you describe should be possible with plant controllers, if I understood correctly. The following
* Control loops 12
# senses dry bulb temperature in sf_bed2.
15 0 0 0 0 # sensor
# plant component 74:pu_sf_bed2 @ node no. 1
-1 74 1 0 # actuator
1 # all daytypes
1 365 # valid Tue-01-Jan - Tue-31-Dec
5 # No. of periods in day: weekdays
14 0 0.000 # ctl type, law (period off), start @
0. # No. of data items
0 8 11.000 # ctl type, law (On-Off control.), start @
7. # No. of data items
1.00000 25.50000 26.50000 0.00800 0.00000 4.00000 0.50000
14 0 14.000 # ctl type, law (period off), start @
0. # No. of data items
0 8 16.000 # ctl type, law (On-Off control.), start @
7. # No. of data items
1.00000 25.50000 26.50000 0.00800 0.00000 4.00000 0.50000
14 0 20.000 # ctl type, law (period off), start @
0. # No. of data items
takes a zone temperature and activates a plant pump (zone 15, plant component number 74, in this case). And this
* Control loops 13
# senses var in compt. 1:theTank @ node no. 1
-1 1 1 0 0 # sensor
# plant component 2:theBoiler @ node no. 1
-1 2 1 0 # actuator
1 # all daytypes
1 365 # valid Tue-01-Jan - Tue-31-Dec
1 # No. of periods in day: weekdays
0 8 0.000 # ctl type, law (On-Off control.), start @
7. # No. of data items
1.00000 38.00000 40.00000 8900.00000 0.00000 0.00000 0.00000
senses a temperature in a plant component (tank) and activates a boiler with 8.9 kW heating capacity (and tries to keep node 1 of the tank between 38 and 40 degC). To get closer to "ideal", you can give the boiler "limitless" power. The controllers are, of course, "on-off", so not really ideal.
I don't know the names of these controllers in the prj menus, though. Maybe the above can help to get some ideas, nonetheless.
Best
Achim
On Dec 3, 2013, at 6:43 PM, Dimitrios Sfakianakis <dimitrios.sfakianakis at strath.ac.uk> wrote:
> Dear List,
>
> I am currently modelling an HVAC system with air re-circulation using explicit plant component modelling. The system is comprised by the basic components: mixing box, cooler, heater, fan and ducts. At a first stage I am not concerned with modelling the actual control system for the heater and cooler (a PID controller) and want to use an ideal controller much like the BLC01 ideal controller in /esrubld/bcfunc.F in order to calculate the power demand of the components.
>
> After going through the available control methodologies for plant components I did not find any controls types that resemble the BLC01. I have tried representing the heater with a thermal zone with an ideal control, connected to the plant network however I notice that if 2 controls are imposed in the same zone, only the second one works.
>
> Is there a plant component controller that can keep the temperature of a component at a certain set point by sensing temperature, activating flux and utilising the required amount of energy? If not what would be the best way to model this in Esp-r?
>
> Thank you for your time.
>
> Kind regards,
>
> Dimitrios Sfakianakis MEng
> Research Assistant, Dept. Naval Architecture and Marine Engineering, University of Strathclyde
> Kelvin Hydrodynamics Laboratory, Acre Road, Glasgow, G20 0TL
> T: +44 (0) 141 330 2648 (Ext 2648)
> M: +44 07514271592
> E: dimitrios.sfakianakis at strath.ac.uk
> The University of Strathclyde is a charitable body, registered in Scotland, with registration number SC015263.
>
>
> _______________________________________________
> esp-r mailing list
> esp-r at lists.strath.ac.uk
> http://lists.strath.ac.uk/mailman/listinfo/esp-r
>
achim.geissler at intergga.ch
More information about the esp-r
mailing list