[esp-r] Re: ESPr validation with gfortran/gcc4

Scott Bucking sbucking at gmail.com
Fri Feb 27 21:07:01 GMT 2009


Hi Alex,

Thanks for your reply.

One more question (with regards to gcc4.1.2/gfortran for Linux).

Did you use a vanilla tool chain (if so what distribution and
version?), or did you compile gcc separately for each test (if so what
enable/disable/with switches did you compile with?)

As I am working on optimization, I need to avoid any numerically induced noise.

Thanks again,

Scott

On Fri, Feb 27, 2009 at 12:37 PM, Ferguson, Alex
<Alex.Ferguson at nrcan-rncan.gc.ca> wrote:
>
>
>>Has anyone recently performed validation on more recent toolchains
>>under a Linux plaform >(gcc4.3/gfortran)?
>>
>>I tend to keep my system updated, and am wondering if a separate
>>version of gcc3/g77 is still necessary to avoid truncation/numerical
>>discrepancies between compilers.
>
> Hi Scott,
>
> We've undertaken validation with gcc/gfortran 4.1 and 4.2, as well as
> the Intel compiler. Results are mixed; 4.1.2 seems the most stable (and
> is now recommended over gcc 3.4.X/ g77, while 4.2+ produces numerical
> exceptions. The next release (11.7) will likely default the Install
> script to use gFortran.
>
> A complete summary of the pre-release testing (including
> g77/gfortran/ifort/sun-f90 comparisons) completed for 11.6 follows.
>
> - Alex
>
> Alex Ferguson
> Sustainable Buildings and Communities (Housing Group)
> CanmetENERGY
> Natural Resources Canada
> P:+1 613 995 3294
> F:+1 613 996 9909
> Alex.Ferguson at NRCan-RNCan.gc.ca
>
>
>
> ======================
> SUMMARY:
> ======================
>
>  - ESP-r compiles correctly on Linux, Cygwin, MinGW, Solaris and OSX.
>  - Portability testing suggests that GCC 4.1.2 builds are actually more
>   reliable than GCC3 builds.
>  - GCC 4.2.3 builds are not as robust.
>  - Some uncertainty remains in Intel builds, as well as builds on OSX.
>
> Recommendations:
>  - Proceed with release 11.6.
>  - The ESP-r 'reference' platform should be changed from
>   Linux / GCC 3.4.6 to Linux / GCC 4.1.2
>  - Cygwin / GCC 3.4.6  and SUN CC builds should continue to be
>   designated as stable
>  - GCC 4.2+ and Intel builds should be used with caution.
>  - Compiler optimization should be used with caution.
>  - OSX / GCC 3.4.6 and MinGW / GCC 3.4.6 builds should be used with
>   caution.
>
> Detailed results follow.
>
>
>
> ======================
> Static Analysis:
> ======================
>
> The Forcheck static analyzer warns of no additional coding errors in the
> current version of pre-release-patches. The total number of errors,
> warnings and informational numbers as declined from the last release.
>
>
>
> ======================
> Regression testing:
> ======================
>
> Changes since the last revision have introduced significant numerical
> differences into the results. But for the first time, all the numerical
> differences were anticipated by developers, and no unintended effects
> were observed during testing.
>
> Two revisions introduced numerical differences in to the results:
>
>  r2838: This commit patched a long-standing bug in the water tank
>        storage model. Predicted water temperatures in the plant
>        network may differ by as much as 3oC; predicted casual gains
>        in the space may differ by as much as 3W.
>
>  r3088: This commit corrected an error in the application of relaxation
>        to the plant network solution scheme. Predicted heat transfer
>        in the plant may differ by as much as 400W (1%), predicted
>        temperatures in the plant may differ by as much as 18oC in
>        extreme cases.
>
> ======================
> Portability testing:
> ======================
> The release candidate can be successfully installed on the following
> platform, compiler and graphics library combinations. We've also added
> support for the Intel compiler suite on linux. Jon Hand has been
> experimenting with support for 64-bit architecture, but this work has
> not yet been generalized for inclusion in the public release.
>
> We've successfully installed ESP-r using the following 32-bit platform,
> compiler and graphics library combinations:
>
>
>
>          Support for ESP-r on various compiler, platform
>                and graphics library combinations.
>    =============================================================
>    Compiler     Library    Linux   Cygwin   MinGW   Sun   OSX
>    =============================================================
>    GCC 3.4.X    X11                                  O     O
>    SUN CC       X11                                  O
>    GCC 3.4.4    X11                  O
>                 noX                  O
>    GCC 3.4.5    noX                           *
>    GCC 3.4.6    X11          O
>                 GTK          O
>                 noX          O
>    INTEL        noX          O
>                 X11          O
>                 GTK          O
>    GCC 4.1.2    X11          O
>    GCC 4.2.3    X11          O
>    -------------------------------------------------------------
>    Notes:
>    O: Installs correctly.
>    *: MinGW only installs correctly to absolute DOS paths
>    (i.e. C:/ESRU)
>    =============================================================
>
>
>
> We've also undertaken a comprehensive comparison of the numerical
> results produced by ESP-r on various platforms. Previously, these
> comparisons were limited to various versions of the GCC compiler suite
> on Linux and cygwin.  Since the last release, Jon Hand has worked to add
> support for XML-enabled builds on OSX and Solaris, using both the GCC
> and Sun compiler suites. Along with new support for the Intel compiler,
> these new capabilities add important reference points for our ongoing
> evaluation of GCC4/gFortran
>
> For the last few years, we've designated GCC 3.4.6/Linux builds as the
> reference version of ESP-r. Most ESP-r development and automated testing
> is based on this platform, and bps's numerical predictions on this
> platform receive scrutiny than any other. GCC 3's fortran 77 compiler
> (g77) has been obsoleted by gFortran, a fortran 90 compiler released
> with GCC 4. Results differ somewhat between g77 and gFortran builds, and
> we've been wondering if they're caused by bugs in g77 or gFortran, or
> perhaps poor ESP-r code that one of the compilers is more sensitive to.
> For the first time, we have additional reference points (Intel and Sun
> CC/f90) to perform these comparisons with.
>
> The following chart summarizes the significant observed differences
> between the  and other platform and compiler combinations. The "Maximum
> difference" reflects the maximum observed difference observed in the
> test cases, excluding exceptional test cases that are discussed in
> section 'Problematic test cases', below..
>
>
>
>      Comparison of results from GCC4.1.2-compiled versions
>      (X11, Linux) with builds from other platform/compilers.
>    =============================================================
>    Arch.     Platform    Compiler      Maximum difference (%)
>    -------------------------------------------------------------
>    IA-32     CYGWIN      GCC 3.4.4            3.18
>              LINUX       GCC 3.4.6            3.18
>                          GCC 4.2.3            0.   (^1)
>                          Intel -O0            0.75 (^2)
>                          Intel -O2           38.781
>    PowerPC   OSX         GCC 3.4             16.1
>    Sparc     SOLARIS     Sun CC/f90           1.80
>    -------------------------------------------------------------
>    NOTES:
>      1. Some test cases produced numerical exceptions and
>         floating point errors. See "Problematic Test Cases".
>      2. One test case produced a larger error (~13%). See below.
>    =============================================================
>
> Detailed scrutiny of the results revealed:
>
>  - gFortran vs Intel iFort / SUN f90
>   ---------------------------------
>   With optimization disabled, the results from SUN and Intel compilers
>   consistently agree more closely with GCC 4.1.2 / gFortran than they
>   do with GCC 3.4.6 / g77. These results suggest GCC 4.1.2 can be used
>   with confidence, and indeed, should be recommended in place of g77.
>
>  - Stability of gFortran
>   ---------------------
>   GCC 4.2.3 builds encounter numerical exceptions in a handful of test
>   cases that ran correctly in all other compilers (See "problematic
>   test cases", below). I recommend GCC 4.2+ builds be regarded as
>   'beta' until this issue is resolved.
>
>  - Intel iFort results: effect of optimization
>   -------------------------------------------
>   With optimization deactivated, the Intel compiler consistently
> produced
>   results close to the gFortran and Sun f90 builds. But when the
> default
>   optimization is activated (using the -O2) option, agreement between
>   the Intel and GCC 4.1.2 compiler deteriorates considerably. Nearly
>   all of the models exhibit small, non-trace differences, and in every
>   case these differences were slightly, or significantly larger than
>   those observed with optimization deactivated.
>
>   Its possible this error is due to bugs in Intel's optimization
>   algorithm, but poor code in ESP-r is more likely the culprit. For
>   instance, when -O0 is specified, the compiler ensures that arguement
>   mismatches in procedure calls are properly converted, but does not
>   perform these conversions by default.
>
>   This problem might occur in GCC builds as well. By default, GCC uses
>   no optimization. I suspect similar issues might appear if -O2 is
>   specified for g77/gFortran builds.
>
>   For these reasons, application of optimization options with ESP-r
>   is not presently recommended.
>
>  - Intel iFort results: test case bld_hc_ISO15099 /HC
>   --------------------------------------------------
>   Newly added for this release, this test case continues to cause
>   headaches. Intel-compiled versions of bps exhibit significant
>   differences from g77/gFortran builds:
>
>      - MAX error (W)                199.37 W  ( 13.293 %)
>      - Predicted value - g77        1499.8 W
>                          Intel      1300.4 W
>        [ observed in:
>          building:zone_05:thermal_loads:net_load:month_01 (max) ]
>
>   The corresponding test case that does not activate the ISO15099
>   correlation does not exhibit the same error, suggesting the Intel
>   compiler is exposing a sensitive compoment of the ISO15099 algorithm,
>
>   or vice-versa.
>
>   The SUN CC/f90 results we have do not include this test case,
>   precluding assessment of whether the g77/gFortran or Intel
> predictions
>   are more accurate. For this reason, the Intel compiler suite is only
>   recommended for beta testing for the time being.
>
>
>  - OSX / GCC builds
>   ----------------
>   A handful of test cases exhibited suprising sensitivity when run
>   with GCC 3.4 compiled builds on OSX. The cause of these differences
>   is not known; OSX builds should be used with caution for the time
>   being.
>
> ===========================
> Problematic test cases
> ===========================
>
>  - esru_benchmark_model / bld_basic_af2_summer
>                        / bld_basic_af2_winter
>   -------------------------------------------
>   We've previously observed the that this coarse-timestep air flow
>   network test case produces significant differences in g77 and
>   gFortran builds. The long, half-hour timesteps cause small
>   differences in the numerical computations to be exaggerated in
>   the aggregated output --- increasing time resolution vastly improves
>   agreement between the compilers.
>
>   The Linux / Intel, Solaris / SUN CC-f90, and OSX / g77 platforms all
>   exhibit the same sensitivity. They produce differing results at
>   short-timesteps, but agreement with Linux / g77 improves at higher
>   time-resolutions.
>
>   Since we've observed that each compiler combination produces
> dissimilar
>   results and that the high-resolution version is more useful,
>   this test case has little value. For this reason, I recommend we
>   delete it.
>
>  - plt_boundary_conditions / connected_flow
>                             connected_temperature
>                             unconnected_controls
>                             unconnected_flow
>                             unconnected_temperature
>   -------------------------------------------------
>   While they run correctly in every other compiler (including GCC
> 4.1.2),
>   these test cases appear to produce numerical exceptions in GCC 4.2.3.
>
>



More information about the esp-r mailing list