[esp-r] Re: Network Flow Nodes and component connections
Ryan Joseph Del Balso
Ryan.Delbalso at Colorado.EDU
Sun Oct 19 01:37:54 BST 2008
Jon and Paul,
Thank you for your help. This does clarify it better than the literature.
One more question though.
Jon, you said the door component works differently than the other
components. This of course is what I am using. I see that it is said that
the adjacent nodes should both be at the same elevation. This confuses me,
because if I have a zone node set at the mid-height of the zone and a
boundary node set at the mid-height of my door, then I cannot have them both
at the same height and I will need a +ve and -ve connection adjustment. I
still have to connect the door to a zone and boundary node so I don't
understand how this works. Can you clarify this a bit more for me?
thanks
Ryan
-----Original Message-----
From: Jon Hand [mailto:jon at esru.strath.ac.uk]
Sent: Saturday, October 18, 2008 6:30 PM
To: Paul Strachan; Ryan Joseph Del Balso; esp-r at lists.strath.ac.uk
Subject: RE: [esp-r] Re: Network Flow Nodes and component connections
Another point of view for flow networks...
During training courses my advise is:
a) imagine you are at the location of the air node
in the room, look at the component. If above you
then the delta height is positive. If you look
down at the component then the delta height is
negative. Do this for each component except for
the bi-directional component (door).
b) One approach to networks is to create one boundary
node for EACH opening/connection to the outside and make the
height of the boundary node at the centre of the
opening. When looking from the point-of-view of
the boundary the delta height is zero.
c) Doors - one of the attributes of a door is the
distance from the bottom of the door to the
adjacent nodes. When using doors in different
size rooms you will have to make additional
door components, each with a distance attribute
that matches the specific room. When using
a door the delta heights are zero because the
component already has the attribute set.
d) There are several exemplar models with flow networks
look at those to check out these patterns.
-Jon Hand
-----Original Message-----
From: esp-r-bounces at lists.strath.ac.uk on behalf of Paul Strachan
Sent: Sat 10/18/2008 4:39 PM
To: Ryan Joseph Del Balso; 'esp-r at lists.strath.ac.uk'
Subject: [esp-r] Re: Network Flow Nodes and component connections
Ryan,
There is a diagram in Jan Hensen's thesis which shows the heights required
for the calculations. See page 4.10 in
http://www.esru.strath.ac.uk/Documents/PhD/hensen_thesis.pdf
Suppose you have a high level opening between 2 zones and that you specify
the connection as a linkage from node X ("positive" node) to node Y
("negative" node). The height of node X is typically placed at the average
height of the zone represented by node X, say 2 m above reference; similarly
for node Y, say 2.5m above reference. If the high level opening is at a
height of 4m above the reference level, then the "Height of +ve linkage
point relative to node X" is +2.0m and the "Height of -ve linkage point
relative to node Y" is +1.5m.
If you had a further low level opening between the 2 zones, say at 1.0m
above reference, then for this connection, the "Height of +ve linkage point
relative to node X" is -1.0m and the "Height of -ve linkage point relative
to node Y" is -1.5m.
Regards
Paul
Ryan Joseph Del Balso wrote:
Can someone clarify the network flow node height and component
connection designations? The cookbook describes placing the node at the
"height" of the opening, but does not define what that height should be. If
I have a door opening, should that height be at the bottom of the opening,
the top or the middle? Also, is the "Height of +ve linkage point relative
to node X" supposed to be from the bottom of the component to the node
height, or from the node height to the bottom of the component? Same with
the -ve linkage node. This would affect the sign. Again, the cookbook and
reference literature do not describe this completely or clearly.
Additionally, the cookbook states that the nodes on either side of
the component should be at the same height, but what if you have a single
interior node and windows as multiple elevations? Then only one of those
nodes could be at the same height as the internal node? I am just a little
confused on this.
Thanks
Ryan
More information about the esp-r
mailing list