The mrt calculation assumes all surfaces are black (emissivity 1.0), as is the sensor cube.  It is a reasonable approximation for most common energy analysis problems.  Where significant differences in surface emissivities exist in a space, a first principles approach would correctly include emissivities in the calculation of mrt.  It seems we do not have this capability, so far.
Jeremy Cockroft, ESRU

________________________________

From: esp-r-bounces at lists.strath.ac.uk [mailto:esp-r-bounces at lists.strath.ac.uk] On Behalf Of Paul Strachan
Sent: 22 May 2008 23:04
To: Francesco Frontini
Cc: esp-r at lists.strath.ac.uk
Subject: [esp-r] Re: R: Mean Radiant Temperature; esp-r Digest, Vol 22, Issue 15


Dear Francesco,

As far as I can ascertain from the ESP-r code, the MRT calculation does not take account of emissivity. The default MRT is simply the area weighted surface temperatures (subroutine MOMNRD in temps.F in esrures). 

It is possible to specify MRT calculations at specific points in the zone (using sensor "cubes"), in which case the calculation includes viewfactors and 4th power radiant exchange (subroutine SENMRT in temps.F in esrures) - but again emissivity is not included. Although rather out-of-date in terms of the user interface, the following publication on the ESRU website gives the basis of the method for user-defined positions for MRT sensors: http://www.esru.strath.ac.uk/Documents/ESPmrt.pdf

Regards
Paul

Francesco Frontini wrote: 

	Dear Jon,
	Ok, 
	but where I can found the fomula used by ESP-r for the MRT calculation?
	Best regards
	Francesco
	
	-----Messaggio originale-----
	Da: esp-r-bounces at lists.strath.ac.uk
	[mailto:esp-r-bounces at lists.strath.ac.uk] Per conto di
	esp-r-request at lists.strath.ac.uk
	Inviato: martedì 20 maggio 2008 13.00
	A: esp-r at lists.strath.ac.uk
	Oggetto: esp-r Digest, Vol 22, Issue 15
	
	Send esp-r mailing list submissions to
		esp-r at lists.strath.ac.uk
	
	To subscribe or unsubscribe via the World Wide Web, visit
		http://lists.strath.ac.uk/mailman/listinfo/esp-r
	or, via email, send a message with subject or body 'help' to
		esp-r-request at lists.strath.ac.uk
	
	You can reach the person managing the list at
		esp-r-owner at lists.strath.ac.uk
	
	When replying, please edit your Subject line so it is more specific than
	"Re: Contents of esp-r digest..."
	
	
	Today's Topics:
	
	   1.  Mean Radiant Temperature (francesco.frontini at polimi.it)
	   2. Re: Mean Radiant Temperature (Geissler Achim)
	   3.  R:   Mean Radiant Temperature (Francesco Frontini)
	   4. Re: R:   Mean Radiant Temperature (Geissler Achim)
	   5. Re: R:   Mean Radiant Temperature (Jon Hand)
	
	
	----------------------------------------------------------------------
	
	Message: 1
	Date: Tue, 20 May 2008 08:45:52 +0200
	From: francesco.frontini at polimi.it
	Subject: [esp-r]  Mean Radiant Temperature
	To: esp-r at lists.strath.ac.uk
	Message-ID: <20080520084552.y2yaryo9kcs880ks at webmail.polimi.it> <mailto:20080520084552.y2yaryo9kcs880ks at webmail.polimi.it> 
	Content-Type: text/plain;	charset=ISO-8859-1;	DelSp="Yes";
		format="flowed"
	
	Dear All,
	I have a question about MRT.
	
	We want to assess the impact on the operative temperature in an office if we
	use an internal blind with a low-emissivity coating (0,5 emissivity for
	indoor-facing surface) instead of 0.9 emissivity.
	We made two different simulation: static (with WIS program) and Dynamic
	(ESP-r).
	
	The results from WIS and from ESP-R for the blind surface temperature are
	consistent (blind temperature about 5K higher for the low-emissivity blind).
	However, the mean radiant temperature at a position close to the blind (0.5
	m in ESP-R) is lower for the high-emissivity blind than the low-emissivity
	blind with the ESP-R calculation.
	Could you please send me the formula that ESP-r uses for the MRT
	calculation? Is there any approximation that would not be appropriate for
	low-emissivity surfaces?
	
	I model the double glazing fa?ade with the internal blind like a single
	construction (no air-ventilation between the glass and the blind). I set the
	U-value for each fa?ade construction (it is similar but not identical for
	the two different solutions, U=0,985+-0,005, obtained from the WIS
	calculation), and the g-value. What changes in the model is the emissivity
	of the indoor-facing surface of the blind
	(e=0,9 for the first case and e=0,5 for the second one!), whereas the
	solar-optical properties remain the same for the two blinds. In the WIS
	model, the emissivity of the two blind surfaces is specified separately.
	For both blinds, the emissivity of the outdoor-facing surface in the WIS
	model is 0.9.
	
	
	Looking forward to your answer and thanking you for your help.
	Any advice and help on this will be much appreciated.
	
	Francesco Frontini
	
	
	
	
	
	
	------------------------------
	
	Message: 2
	Date: Tue, 20 May 2008 09:22:39 +0200
	From: "Geissler Achim" <Achim.Geissler at josef-gartner.ch> <mailto:Achim.Geissler at josef-gartner.ch> 
	Subject: [esp-r] Re: Mean Radiant Temperature
	To: <francesco.frontini at polimi.it> <mailto:francesco.frontini at polimi.it> ,	<esp-r at lists.strath.ac.uk> <mailto:esp-r at lists.strath.ac.uk> 
	Message-ID:
		<5410907208A9F149ADB6E44744892B3C45EBE8 at sgartgum1.gart.intra> <mailto:5410907208A9F149ADB6E44744892B3C45EBE8 at sgartgum1.gart.intra> 
	Content-Type: text/plain;	charset="iso-8859-1"
	
	Dear Francesco,
	
	  

		We want to assess the impact on the operative temperature in an office 
		if we use an internal blind with a low-emissivity coating (0,5 
		emissivity for indoor-facing surface) instead of 0.9 emissivity.
		We made two different simulation: static (with WIS program) and 
		Dynamic (ESP-r).
		    

	
	  

		The results from WIS and from ESP-R for the blind surface temperature 
		are consistent (blind temperature about 5K higher for the 
		low-emissivity blind).
		    

	That is good news.
	
	  

		However, the mean radiant temperature at a position close to the blind 
		(0.5 m in ESP-R) is lower for the high-emissivity blind than the 
		low-emissivity blind with the ESP-R calculation.
		    

	
	As the mean radiant temperature is defined by view factors and surface
	temperature, only, all is well, no? The low-e blind has a higher
	temperature, thus I would expect the mean radiant temperature close to the
	blind to be higher. That is what you seem to have obtained as result?
	
	Best regards,
	Achim
	
	
	
	
	
	------------------------------
	
	Message: 3
	Date: Tue, 20 May 2008 10:35:15 +0200
	From: "Francesco Frontini" <francesco.frontini at polimi.it> <mailto:francesco.frontini at polimi.it> 
	Subject: [esp-r]  R:   Mean Radiant Temperature
	To: "'Geissler Achim'" <Achim.Geissler at josef-gartner.ch> <mailto:Achim.Geissler at josef-gartner.ch> ,
		<esp-r at lists.strath.ac.uk> <mailto:esp-r at lists.strath.ac.uk> 
	Message-ID:
		
	<!~!UENERkVCMDkAAQACAAAAAAAAAAAAAAAAABgAAAAAAAAAru7KqoPmvUiwJBhxMD9pLMKAAAAQ
	AAAAq+fYsqTr4E+5QjbiDeTAbQEAAAAA at polimi.it>
		
	Content-Type: text/plain;	charset="iso-8859-1"
	
	Dear Achim
	Yes I have obtained a MRT, close to the blind, higher for the solution with
	low-e blind (that has a higer surface temperature). But for my opinion the
	MRT has to take into account not only the view factor and the temperature of
	the surface but also the emissivity. For that reason I'm also supposing that
	with a low emmissivity also the MRT should be low (for exemple if the view
	factor is the same: 43,88?x0,9>48.21?x0,5! Where the formula is
	(T1(?C)blind)*(emissivity(1))>(T2(?C)blind)*(emissivity(2))!!!). It's not
	correct?
	
	Best regards,
	Francesco
	
	-----Messaggio originale-----
	Da: Geissler Achim [mailto:Achim.Geissler at josef-gartner.ch]
	Inviato: marted? 20 maggio 2008 9.23
	A: francesco.frontini at polimi.it; esp-r at lists.strath.ac.uk
	Oggetto: RE: [esp-r] Mean Radiant Temperature
	
	Dear Francesco,
	
	  

		We want to assess the impact on the operative temperature in an office 
		if we use an internal blind with a low-emissivity coating (0,5 
		emissivity for indoor-facing surface) instead of 0.9 emissivity.
		We made two different simulation: static (with WIS program) and 
		Dynamic (ESP-r).
		    

	
	  

		The results from WIS and from ESP-R for the blind surface temperature 
		are consistent (blind temperature about 5K higher for the 
		low-emissivity blind).
		    

	That is good news.
	
	  

		However, the mean radiant temperature at a position close to the blind
		(0.5 m in ESP-R) is lower for the high-emissivity blind than the 
		low-emissivity blind with the ESP-R calculation.
		    

	
	As the mean radiant temperature is defined by view factors and surface
	temperature, only, all is well, no? The low-e blind has a higher
	temperature, thus I would expect the mean radiant temperature close to the
	blind to be higher. That is what you seem to have obtained as result?
	
	Best regards,
	Achim
	
	
	
	
	
	------------------------------
	
	Message: 4
	Date: Tue, 20 May 2008 11:33:33 +0200
	From: "Geissler Achim" <Achim.Geissler at josef-gartner.ch> <mailto:Achim.Geissler at josef-gartner.ch> 
	Subject: [esp-r] Re: R:   Mean Radiant Temperature
	To: "Francesco Frontini" <francesco.frontini at polimi.it> <mailto:francesco.frontini at polimi.it> ,
		<esp-r at lists.strath.ac.uk> <mailto:esp-r at lists.strath.ac.uk> 
	Message-ID:
		<5410907208A9F149ADB6E44744892B3C45EC09 at sgartgum1.gart.intra> <mailto:5410907208A9F149ADB6E44744892B3C45EC09 at sgartgum1.gart.intra> 
	Content-Type: text/plain;	charset="iso-8859-1"
	
	Dear Francesco,
	the definitions I know of for mean radiant temperature do not take
	emissivity into account. The interesting question probably is, is the
	measure "MRT" useful for environments with large differences in emissivity?
	Of course, for radiation heat transfer, the emissivity is important (that is
	what I think you want to describe?).
	I would assume that the definition of MRT is based on the "normal" case,
	that all surfaces of an indoor space have an emissivity of approx. 0.9.
	Thus, the description of the radiative surroundings by temperature alone is
	sufficient.
	For your case, you may need to define a "new" MRT - maybe more a "mean
	radiant heat exchange" type of coefficient (or try PPD / PMV calculations,
	however, these also use standard mean radiant temperature for their
	calculation).
	Regards,
	Achim
	
	
	  

		-----Original Message-----
		From: esp-r-bounces at lists.strath.ac.uk [mailto:esp-r- 
		bounces at lists.strath.ac.uk] On Behalf Of Francesco Frontini
		Sent: Tuesday, May 20, 2008 10:35 AM
		To: Geissler Achim; esp-r at lists.strath.ac.uk
		Subject: [esp-r] R: Mean Radiant Temperature
		
		Dear Achim
		Yes I have obtained a MRT, close to the blind, higher for the solution 
		with low-e blind (that has a higer surface temperature). But for my 
		opinion the MRT has to take into account not only the view factor and 
		the temperature of the surface but also the emissivity. For that 
		reason I'm also supposing that with a low emmissivity also the MRT 
		should be low (for exemple if the view factor is the same: 
		43,88?x0,9>48.21?x0,5! Where the formula is 
		(T1(?C)blind)*(emissivity(1))>(T2(?C)blind)*(emissivity(2))!!!). It's 
		not correct?
		
		Best regards,
		Francesco
		
		-----Messaggio originale-----
		Da: Geissler Achim [mailto:Achim.Geissler at josef-gartner.ch]
		Inviato: marted? 20 maggio 2008 9.23
		A: francesco.frontini at polimi.it; esp-r at lists.strath.ac.uk
		Oggetto: RE: [esp-r] Mean Radiant Temperature
		
		Dear Francesco,
		
		    

			We want to assess the impact on the operative temperature in an 
			office if we use an internal blind with a low-emissivity coating 
			(0,5 emissivity for indoor-facing surface) instead of 0.9 emissivity.
			We made two different simulation: static (with WIS program) and 
			Dynamic (ESP-r).
			      

			The results from WIS and from ESP-R for the blind surface 
			temperature are consistent (blind temperature about 5K higher for 
			the low-emissivity blind).
			      

		That is good news.
		
		    

			However, the mean radiant temperature at a position close to the 
			blind
			(0.5 m in ESP-R) is lower for the high-emissivity blind than the 
			low-emissivity blind with the ESP-R calculation.
			      

		As the mean radiant temperature is defined by view factors and surface 
		temperature, only, all is well, no? The low-e blind has a higher 
		temperature, thus I would expect the mean radiant temperature close to 
		the blind to be higher. That is what you seem to have obtained as result?
		
		Best regards,
		Achim
		
		
		
		_______________________________________________
		esp-r mailing list
		esp-r at lists.strath.ac.uk
		http://lists.strath.ac.uk/mailman/listinfo/esp-r
		    

	
	
	
	------------------------------
	
	Message: 5
	Date: Tue, 20 May 2008 11:36:21 +0100
	From: Jon Hand <jon at esru.strath.ac.uk> <mailto:jon at esru.strath.ac.uk> 
	Subject: [esp-r] Re: R:   Mean Radiant Temperature
	To: "Geissler Achim" <Achim.Geissler at josef-gartner.ch> <mailto:Achim.Geissler at josef-gartner.ch> ,	"Francesco
		Frontini" <francesco.frontini at polimi.it> <mailto:francesco.frontini at polimi.it> ,
	<esp-r at lists.strath.ac.uk> <mailto:esp-r at lists.strath.ac.uk> 
	Message-ID:
		<B94620A0857DFE4DB194C4A2DBDC088F8B5FD6 at BE-SCAM2.ds.strath.ac.uk> <mailto:B94620A0857DFE4DB194C4A2DBDC088F8B5FD6 at BE-SCAM2.ds.strath.ac.uk> 
	Content-Type: text/plain; charset="iso-8859-1"
	
	
	There is a radiant asymmetry report as part of the comfort report and I
	think that will be taking account of the emissivity.
	
	There is an esp-r model which deals with a heated ceiling panel and location
	specific comfort for a patient in a bed which needs to be added as an
	exemplar model. 
	
	-Jon Hand
	
	
	-----Original Message-----
	From: esp-r-bounces at lists.strath.ac.uk on behalf of Geissler Achim
	Sent: Tue 5/20/2008 10:33 AM
	To: Francesco Frontini; esp-r at lists.strath.ac.uk
	Subject: [esp-r] Re: R:   Mean Radiant Temperature
	 
	Dear Francesco,
	the definitions I know of for mean radiant temperature do not take
	emissivity into account. The interesting question probably is, is the
	measure "MRT" useful for environments with large differences in emissivity?
	Of course, for radiation heat transfer, the emissivity is important (that is
	what I think you want to describe?).
	I would assume that the definition of MRT is based on the "normal" case,
	that all surfaces of an indoor space have an emissivity of approx. 0.9.
	Thus, the description of the radiative surroundings by temperature alone is
	sufficient.
	For your case, you may need to define a "new" MRT - maybe more a "mean
	radiant heat exchange" type of coefficient (or try PPD / PMV calculations,
	however, these also use standard mean radiant temperature for their
	calculation).
	Regards,
	Achim
	
	
	  

		-----Original Message-----
		From: esp-r-bounces at lists.strath.ac.uk [mailto:esp-r- 
		bounces at lists.strath.ac.uk] On Behalf Of Francesco Frontini
		Sent: Tuesday, May 20, 2008 10:35 AM
		To: Geissler Achim; esp-r at lists.strath.ac.uk
		Subject: [esp-r] R: Mean Radiant Temperature
		
		Dear Achim
		Yes I have obtained a MRT, close to the blind, higher for the solution 
		with low-e blind (that has a higer surface temperature). But for my 
		opinion the MRT has to take into account not only the view factor and 
		the temperature of the surface but also the emissivity. For that 
		reason I'm also supposing that with a low emmissivity also the MRT 
		should be low (for exemple if the view factor is the same: 
		43,88?x0,9>48.21?x0,5! Where the formula is 
		(T1(?C)blind)*(emissivity(1))>(T2(?C)blind)*(emissivity(2))!!!). It's 
		not correct?
		
		Best regards,
		Francesco
		
		-----Messaggio originale-----
		Da: Geissler Achim [mailto:Achim.Geissler at josef-gartner.ch]
		Inviato: marted? 20 maggio 2008 9.23
		A: francesco.frontini at polimi.it; esp-r at lists.strath.ac.uk
		Oggetto: RE: [esp-r] Mean Radiant Temperature
		
		Dear Francesco,
		
		    

			We want to assess the impact on the operative temperature in an 
			office if we use an internal blind with a low-emissivity coating 
			(0,5 emissivity for indoor-facing surface) instead of 0.9 emissivity.
			We made two different simulation: static (with WIS program) and 
			Dynamic (ESP-r).
			      

			The results from WIS and from ESP-R for the blind surface 
			temperature are consistent (blind temperature about 5K higher for 
			the low-emissivity blind).
			      

		That is good news.
		
		    

			However, the mean radiant temperature at a position close to the 
			blind
			(0.5 m in ESP-R) is lower for the high-emissivity blind than the 
			low-emissivity blind with the ESP-R calculation.
			      

		As the mean radiant temperature is defined by view factors and surface 
		temperature, only, all is well, no? The low-e blind has a higher 
		temperature, thus I would expect the mean radiant temperature close to 
		the blind to be higher. That is what you seem to have obtained as result?
		
		Best regards,
		Achim
		
		
		
		_______________________________________________
		esp-r mailing list
		esp-r at lists.strath.ac.uk
		http://lists.strath.ac.uk/mailman/listinfo/esp-r
		    

	


-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.strath.ac.uk/archives/esp-r/attachments/20080523/02549844/attachment-0001.html 


More information about the esp-r mailing list